SMH-II-2.2KW-12V-WIFI Inverter Setup Guide for Ireland

This article provides a detailed guide on configuring the SMH-II-2.2KW-12V-WIFI inverter for a solar-powered off-grid or hybrid system in Ireland. The configuration is based on a 12V system using LiFePO4 (Lithium Iron Phosphate) batteries and solar panels, specifically suited to Ireland’s electrical grid and climatic conditions.

System Overview

Battery System:

  • Battery Type: LiFePO4 (Lithium Iron Phosphate)
  • Capacity: 12V 100Ah (4 x 3.2V 100Ah cells in series)
  • Nominal Voltage: 12.8V
  • Fully Charged Voltage: 14.6V
  • BMS: 4S 12V 100A LiFePO4 BMS

Solar Panels:

  • Topsolar 200W Panels (Two Kits = 4 panels total) this setup is for limited space
  • Panel Configuration: Series connection to reach higher voltages for optimal inverter operation
  • Maximum Output Power: 800W total (4 x 200W)

Location-Specific Configuration:

  • Ireland operates on 230V and 50Hz AC output.

Recommended Inverter Settings

Here are the recommended settings for the SMH-II-2.2KW-12V-WIFI inverter to optimize performance based on your battery, solar panel setup, and Ireland’s grid standards:

Program No. Setting Description
00 ESC Exit setting mode
01 SBU Prioritizes solar and battery before using utility power (Solar-Battery-Utility)
02 60A Maximum charging current from solar/utility (based on BMS specifications)
03 APL AC input voltage range for appliances (wide range, ideal for home use)
04 SdS Power-saving mode disabled
05 USE User-defined battery type (for custom LiFePO4 settings)
06 Lrd Auto-restart after overload disabled (optional based on preferences)
07 tEd Auto-restart after overheating disabled (optional)
08 220V Output voltage set to 220V (Ireland uses 230V, so this is within range)
09 50Hz Output frequency set to 50Hz (Ireland’s standard)
10 PAC Set maximum utility charging current (30A or 60A depending on setup)
11 30A Utility charging current based on your battery specifications
12 11.5V Voltage for switching back to utility power (discharge threshold)
13 12.8V Voltage for switching back to battery mode when SBU is selected
16 CSO Charger source priority (Solar first)
17 60A Maximum charging current from AC source
18 bON Alarm control enabled (optional)
19 ESP Auto-return to default display enabled (after 1 minute of inactivity)
20 LON LCD backlight control enabled
21 AON Beep when primary power source is interrupted
22 bLd Overload bypass disabled
23 FEN Record fault codes for troubleshooting

Battery Charging Settings

Program No. Setting Description
26 14.1V Bulk charging voltage for fast charging
27 13.5V Floating voltage to maintain charge without overcharging
29 10.5V Low DC cutoff voltage to prevent battery damage

Battery Equalization Settings (Not Recommended for LiFePO4)

Program No. Setting Description
33 EdS Battery equalization disabled (LiFePO4 batteries do not require equalization)
39 AdS Equalization activated immediately (Ensure this is disabled)

Download the Manual here:

Conclusion

For your setup, using 4 Topsolar 200W panels in series ensures the inverter operates within its MPPT voltage range. The battery system, configured with a LiFePO4 battery pack, is optimized for long life and stable operation. Make sure to configure the inverter’s settings as per the table above for best performance in Ireland’s electrical grid.

If you have any questions about these settings or your system’s configuration, feel free to ask in the comments!